Replies: 4 comments 8 replies
-
Fixed in abb13d9 For the reboot every 5 seconds, can you give some logs or more details ? |
Beta Was this translation helpful? Give feedback.
-
PID was not tested very long on my side. |
Beta Was this translation helpful? Give feedback.
-
Hello, I have an important question: I have actuators from dtn thermotune 2. I measured the resistance, 27.5 ohms. This gave me the standard bemf value of 0.105. All control valves do the same thing: when they are open and I close them, they close to about 50% and then it reaches the bemf trigger, they stop and show closed. When I then open them again, the same thing happens. It opens to about 50% and then the trigger comes, it stops and shows closed. Is that normal or can I set somewhere how far the maximum travel should be? The most important thing: the valve only opens in the first 10% from closed to open. So at 5% it is about half open and at 10 it is already fully open. |
Beta Was this translation helpful? Give feedback.
-
Beta Was this translation helpful? Give feedback.
-
after using tanh same days i try to test pid. but first of all: i hat to add climate_id: PID_CH${channel_number} 4times and change default_target_temperature:_low to default_target_temperature
but now it seems to resarts every 5 seconds
Beta Was this translation helpful? Give feedback.